beautypg.com

Clear faults detected by psh, Clear faults – FUJITSU SPARC T5440 User Manual

Page 75

background image

Managing Faults

49

▼ Clear Faults Detected by PSH

When the Solaris PSH facility detects faults, the faults are logged and displayed on
the console. In most cases, after the fault is repaired, the corrected state is detected by
the system and the fault condition is repaired automatically. However, this repair
should be verified. In cases where the fault condition is not automatically cleared, the
fault must be cleared manually.

1. After replacing a faulty FRU, power on the server.

2. At the ILOM prompt, use the show faulty command to identify PSH-detected

faults.

If no fault is reported, you do not need to do anything else. Do not perform the
subsequent steps.

If a fault is reported, perform

Step 3

and

Step 4

.

3. Use the clear_fault_action property of the FRU to clear the fault from the

service processor. For example:

4. Clear the fault from all persistent fault records.

In some cases, even though the fault is cleared, some persistent fault information
remains and results in erroneous fault messages at boot time. To ensure that these
messages are not displayed, perform the following Solaris command:

fmadm repair

UUID

Example:

/SP/faultmgmt/0 | timestamp | Dec 21 16:40:56

/SP/faultmgmt/0/ | timestamp | Dec 21 16:40:56

faults/0 | |

/SP/faultmgmt/0/ | sp_detected_fault | /SYS/MB/CPU0/CMP0/BR1/CH0/D0

faults/0 | | Forced fail(POST)

-> set /SYS/MB/CPU0/CMP0/BR0/CH0/D0 clear_fault_action=True

Are you sure you want to clear /SYS/MB/CPU0/CMP0/BR0/CH0/D0 (y/n)? y

Set ’clear_fault_action’ to ’true

# fmadm repair 7ee0e46b-ea64-6565-e684-e996963f7b86

CODE EXAMPLE:

Fault Detected by POST (Continued)