34

SPARC Enterprise T5440 Server Service Manual • July 2009

Example of the show faulty command displaying an environmental fault:

Example of the show faulty command displaying a configuration fault:

Note –

Environmental and configuration faults automatically clear when the

environmental condition returns to the normal range of when the configuration fault
is addressed.

Example showing a fault that was detected by the PSH technology. These kinds
of faults are distinguished from other kinds of faults by the presence of a
sunw-msg-id

and by a UUID.

-> show faulty

Target

| Property

| Value

--------------------+------------------------+-------------------------------

/SP/faultmgmt/0 | fru | /SYS/MB/FT1

/SP/faultmgmt/0 | timestamp | Dec 14 23:01:32

/SP/faultmgmt/0/ | timestamp | Dec 14 23:01:32 faults/0

/SP/faultmgmt/0/ | sp_detected_fault | TACH at /SYS/MB/FT1 has

faults/0 | | exceeded low non-recoverable

| | threshold.

-> show faulty

Target | Property | Value

------------------+----------------------+-----------------------------------

/SP/faultmgmt/0 | fru | /SYS

/SP/faultmgmt/0 | timestamp | Mar 17 08:17:45

/SP/faultmgmt/0/ | timestamp | Mar 17 08:17:45

faults/0 | |

/SP/faultmgmt/0/ | sp_detected_fault | At least 2 power supplies must

faults/0 | | have AC power

-> show faulty

Target

| Property

| Value

--------------------+------------------------+--------------------------------

/SP/faultmgmt/0 | fru | /SYS/MB/MEM0/CMP0/BR1/CH1/D1

/SP/faultmgmt/0 | timestamp | Dec 14 22:43:59

/SP/faultmgmt/0/ | sunw-msg-id | SUN4V-8000-DX

faults/0 | |

/SP/faultmgmt/0/

| uuid

| 3aa7c854-9667-e176-efe5-e487e520

faults/0

|

| 7a8a

/SP/faultmgmt/0/

| timestamp

| Dec 14 22:43:59

faults/0 | |