84

SPARC Enterprise T5440 Server Service Manual • July 2009

▼ Install a Fan Tray

1. Slide each fan tray into its bay until it locks into place.

Ensure that the fan tray is oriented correctly. Airflow in the system is from front to
back.

2. Verify proper fan tray operation.

See

“Fan Tray Fault LED” on page 84

.

Next Steps

If you are replacing the fan trays after performing another service procedure,
complete these steps.

“Slide the Server Into the Rack” on page 151

“Power On the Server” on page 153

Fan Tray Device Identifiers

TABLE: Fan Tray Device Identifiers on page 84

describes the FRU device names for

the fan trays in the server.

Related Information

“Managing Faults” on page 9

“Hot-Pluggable and Hot-Swappable Devices” on page 72

“Fan Tray Fault LED” on page 84

Fan Tray Fault LED

Each fan tray contains a Fault LED that is located on the top panel of the server. The
LED is visible when you slide the server partially out of the rack.

TABLE:

Fan Tray Device Identifiers

Device

Device Identifier

FT0

/SYS/MB/FT0

FT1

/SYS/MB/FT1

FT2

/SYS/MB/FT2

FT3

/SYS/MB/FT3