Servicing the fan tray carriage, Related information, Remove the fan tray carriage – FUJITSU SPARC T5440 User Manual
Page 155

Servicing Field-Replaceable Units
129
Servicing the Fan Tray Carriage
You must remove the fan tray carriage in order to service the following components:
■
Hard disk backplane
■
Motherboard
■
Front control panel
■
Front I/O board
Related Information
■
“Servicing Fan Trays” on page 81
■
“Servicing the Hard Drive Backplane” on page 132
■
“Servicing the Motherboard” on page 135
■
“Servicing the Front Control Panel” on page 144
■
“Servicing the Front I/O Board” on page 146
▼ Remove the Fan Tray Carriage
Before you begin, complete these tasks:
■
Read the section,
“Safety Information” on page 59
■
Power off the server using one of the methods described in the section,
.
■
“Extend the Server to the Maintenance Position” on page 66
■
“Perform Electrostatic Discharge – Antistatic Prevention Measures” on page 69
■
“Remove a Fan Tray” on page 83
Note –
You must remove all four fan trays.
■
“Remove the Top Cover” on page 69
■
“Remove a CMP/Memory Module” on page 99
Note –
You must remove all CPU modules and memory modules from the system.
Do the following: