Related information – FUJITSU SPARC T5120 User Manual
Page 154

128
SPARC Enterprise T5120 and T5220 Servers Service Manual • July 2009
FIGURE:
Installing a Fan Module
2. Apply firm pressure to fully seat the fan module.
3. Verify that the Fan Fault LED on the replaced fan module is off.
4. Close the top cover door.
5. Verify that the system Fan Fault LED, Service Required LEDs, and the
individual fan module Fault LED are off.
6. Run the ILOM show faulty command to verify that the fan fault has been
cleared.
See
“Detecting Faults With ILOM” on page 22
for more information on using the
show faulty
command.
Related Information
■
“Extend the Server to the Maintenance Position” on page 63
■
This manual is related to the following products: