Troubleshooting 30

Output Load Level LED is red or flashing red

Action:

1.

Remove one or more load devices to reduce the power requirements.

2.

Initiate a self-test ("

Initiating a self-test

" on page

19

).

3.

If the condition persists, verify that the load devices are not defective.

Battery Charge LED is red

Action:

If the Power LED is flashing green:

a.

Save your work, and power down the UPS ("

Powering down the UPS

" on page

19

).

b.

After the blackout or brownout is over, power up the UPS ("

Powering up the UPS

" on page

18

).

c.

Allow the UPS batteries to charge for 24 hours.

If the Power LED is green:

a.

Continue to let the batteries charge until the Battery Charge LED is green.

b.

Initiate a self-test ("

Initiating a self-test

" on page

19

).

Battery Warning LED is amber

Action:

1.

Allow the UPS batteries to charge for 24 hours.

2.

Initiate a self-test ("

Initiating a self-test

" on page

19

).

Site Wiring Fault LED is red

Action: Contact a qualified electrician to be sure that:

The utility power receptacle is grounded.

There is a ground wire in the UPS power cord.

The line and neutral wires are not reversed in the wall outlet.