Ups does not provide the expected backup time, Ups emits a slight clicking noise, Power led flashes – HP T1000 User Manual
Page 29: Voltage configuration led is green, 29 ups does not provide the expected backup time, 29 ups emits a slight clicking noise, 29 power led flashes, 29 voltage configuration led is green
Troubleshooting 29
UPS frequently switches between utility and battery power
Action:
1.
Check the input voltage and reconfigure the UPS ("
Selecting the UPS voltage configuration
2.
Contact a qualified electrician to verify that the utility power is suitable for the UPS.
UPS does not provide the expected backup time
Action:
1.
If the Output Load Level LED is red or flashing red, remove one or more load devices to reduce the
power requirements.
2.
" on page
3.
Verify that the batteries are connected.
4.
Allow the UPS batteries to charge for 24 hours.
5.
Initiate a self-test ("
" on page
6.
During extended power outages, save your work, power down the load devices, and then power
down the UPS ("
) to conserve battery power.
UPS emits a slight clicking noise
Action: The UPS is automatically correcting high or low AC voltage on the utility line. No action is
required.
Power LED flashes
Action:
If the Battery Charge LED is also red:
a.
Save your work, and power down the UPS ("
b.
After the blackout or brownout is over, power up the UPS ("
c.
Allow the UPS batteries to charge for 24 hours.
If the Battery Charge LED is also yellow or green:
a.
Consider saving your work and powering down the UPS (on page
brownout is prolonged, the Battery Charge LED turns red as the UPS batteries near depletion.
b.
After the blackout or brownout is over, power up the UPS ("
c.
Allow the UPS batteries to charge for 24 hours.
Voltage Configuration LED is green
Action: The UPS is automatically correcting high or low AC voltage on the utility line. No action is
required.