T6570, T8570 SERIES DIGITAL FAN-COIL THERMOSTATS

Table 5. Thermostat Parameter Options

Parameter

ID

Description

°C Scale

°F Scale

Default

Values

Default

Values

Temperature Scale tS

Allows selection of either °C or °F scale Yes

No

Dead Band

db

Setting deadband (Zero Energy Band) 2

2, 3, 4

4

3, 4, 5

Heat or Cool

Operating Mode

OP

Setting operating mode on single relay,

non-changeover models, to either Heat

or Cool

0

0: cool

1: heat

0

0: cool

1: heat

Unoccupied Cooling

Setpoint

uC

Program unoccupied cooling setpoint

for energy savings.

25

25 to 30

77

77 to 90

Unoccupied Heating

Setpoint

uH

Program unoccupied heating setpoint

for energy savings

18

10 to 18

65

50 to 65

Minimum Cooling

Off Time

CO Setting cooling off-time for short cycle

prevention.

0

0, 3, 4, 5

0

0, 3, 4, 5

Minimum Heating

Off Time

HO Setting heating off-time for short cycle

prevention.

0

0, 3, 4, 5

0

0, 3, 4, 5

Minimum Cooling

Setpoint (Low Limit)

CL

Sets the minimum allowable cooling

setpoint.

10

10 to 30

50

50 to 90

Maximum Heating

Setpoint (High Limit)

HL

Sets the maximum allowable heating

setpoint.

30

10 to 30

90

50 to 90

Energy Savings

Configuration

ES

Activate energy savings mode by a

choice of either contact closure or

contact opening.

1

1: normally open

0: normally closed

1

1: normally open

0: normally closed

Display of Room

Temperature

rt

Allows installer to restrict temperature

display to set point only. With this

parameter, the unit will only display the

set point temperature. Useful where

setpoint limits (HL and CL) will affect

control performance and Room

Temperature display will disagree with

user setpoint.

1

1: room temp.

0: setpoint only

1

1: room temp.

0: setpoint only

WIRING

Table 6. Leadwire Color Code (if fitted)

Terminal

Color

Use

1

Black (BK)

L1 (Hot)

2

White (WH)

L2 (N)

3

Orange (OR)

Heat

4

Yellow (YL)

Cool

5

Gray (GY)

Damper

6

Violet (VI)

Fan Common

7

Red (RD)

Fan Low

8

Blue (BU)

Fan Medium

9

Brown (BN)

Fan High

10

Energy Mgt.

System

11

Fig. 6. Wiring 2-pipe cool-only thermostat with fan On/Auto

switch.

7

95C-10897–6