T6570, T8570 SERIES DIGITAL FAN-COIL THERMOSTATS

Mounting

Any T6570, T8570 series thermostat can be mounted directly

on the wall on a 65x65mm junction box, or a 2"x4" horizontal

junction box. An optional adapter plate is available for

mounting on a 4"x4" or vertical junction box. (See Fig. 2)

Mounting screws are supplied for alternatives.

1. Feed leadwires through wiring access hole of wallplate

and adaptor plate (if used).

2. Attach supply wires using wire nuts (not provided), or

screw terminals, as appropriate.

3. Locate wallplate in the horizontal mounting position. See

Fig. 2 if using the vertical junction box adapter plate.

4. Push leadwires into electrical junction box and attach

wallplate to box using machine screws provided in the

appropriate mounting holes.

5. Attach thermostat to wallplate:

a. Locate the two center side holes on the back of the

thermostat.

b. Align the holes with the two wallplate side tabs.

c. Press down firmly to snap thermostat into place.

M17505

Fig. 2. Mounting the vertical junction box adapter plate

M17505 Optional adapter plate.

Removing the thermostat

CAUTION

Equipment Damage Hazard.

Improper removal can damage the thermostat.

Carefully follow the thermostat removal directions.

If it is necessary to remove the thermostat from the wallplate

(see Fig. 3):

1. Use a screwdriver to pry thermostat left side away from

the base.

2. Use the screwdriver to pry thermostat's right side away

from the wallplate.

3. Use both hands to pull the thermostat straight away from

the wallplate.

1

2

3

M15396

Fig. 3. Removing the thermostat

Thoroughly check wiring to the wallplate before finally

mounting the thermostat on the wall.

OPERATION

Control

PROPORTIONAL + INTEGRAL (P+I) CONTROL
Like a mechanical thermostat, the T6570, T8570 Series have

On/Off control output. However, this output is regulated by a

P+I algorithm, enabling the thermostat to control closer to

setpoint than conventional thermostats. This results in

performance where the space temperature is maintained within

0.75°C (1.5°F) of the setpoint regardless of fan speed.

P+I action minimizes the difference between the temperature

setpoint and the effective control point by adjusting the output

on-time until the control point matches the setpoint. The on-

time is based on a fixed cycle rate of 4 cycles/hour for cooling

(8 cycles/hour for heating), and the proportional band is 1.6°C

(2.9°F).

NOTE: Integral action corrects the temperature control errors

of proportional-only control, but it is slower to react to

large temperature or setpoint changes.

These thermostats also feature optional built-in time

delays for equipment protection which can inhibit

rapid response to large setpoint changes if active.

SINGLE-STAGE COOLING OR HEATING CONTROL (SEE FIG. 4)
In cooling mode the user setpoint will be positioned at the

bottom of the Proportional Band, so the setpoint will effectively

be the temperature where the cooling switches off. In heating

mode the user setpoint will be positioned at the top of the

Proportional Band, and this will be the temperature where the

heating switches off.

NOTE: This also applies to models with manual heat/cool

changeover.