POWER
SUPPLY
A
/К PROVIDE DISCONNECT MEANS AND OVERLOAD
PROTECTION AS REQUIRED.
Fig. 8--Typical hookup of T6052A to control two
stage heating system.
A\
PROVIDE DISCONNECT MEANS AND OVERLOAD
PROTECTION AS REQUIRED.
Fig. 9—Typical hookup of T6052A to control two
stage cooling system.
POWER
SUPPLY
A
Д PROVIDE DISCONNECT MEANS AND OVERLOAD
PROTECTION AS REQUIRED.
Fig. 10—Typical hookup of T6052B to control heating
cooling system with auto changeover.
Each notch on the calibration mechanism represents
2,000 feet. If you are above sea level use the chart to
determine how far to move the indicator:
ALTITUDE CALIBRATION
This thermostat was calibrated at the factory for
accuracy at 1,000 feet above sea level. It may be nec
essary to reset the thermostat for the altitude of your
locality. If you do not know your altitude, consult your
local U.S. Weather Bureau or Public Library.
POWER
SUPPLY
Elevation (in feet)
Indicator
A
0 to 2,000
Leave as is
2,000 to 4,000
Move down 1 notch
4,000 to 6,000
Move down 2 notches
6,000 and above
Move down 3 notches
OPERATION AND CHECKOUT------------------------
After the thermostat is installed and wired, operate
it manually to make certain it is connected properly.
Checkout will depend on type of hookup and controlled
equipment. For cooling control check, turn the setting
knob to move the indicator down the scale. This ini
tiates a call for cooling and the cooling equipment
should respond. For heating control check, turn the
setting knob to move the indicator up the scale. This
initiates a call for heat, and the heating equipment
should respond. For heating/cooling control, check
both heating and cooling as described above. For
Series 60 control check, cycle the equipment through
the T6051A and make sure it functions as intended.
CAUTION
If the thermostat is controlling a compressor, allow
at least two minutes between on cycles to equalize
the internal pressure. Rapid cycling might damage
the compressor and overload the electrical circuit.
TO LOCK
After altitude adjustment is complete, replace the
cover and set cover screw with set point knob. With
the knob again in place, move the set point indicator
to the desired temperature setting. Remove the set
point knob to lock the set point.