Day night mode t560 only, Power limit input analog 0 to 10 vdc, Output #3 tri-state floating – Viconics T560 User Manual

Page 2

background image

Page: 4

Page: 5

Page: 6

ORDER CODE

T510

-

AB

-

CD

-

EF

-

GH

( without day-night mode )

T560

-

AB

-

CD

-

EF

-

GH

( with day-night mode )

A

Output no. 1 ( controlled device )

Type

0

Not installed

5

"SSR" with 3-32 Vdc input

Pulsed 0/5 Vdc

6

0 to 10 Vdc actuator, voltage relay or "SCR" *

0 to 10 Vdc

7

0 to 10 Vdc high cooling signal for Vdc relay

Higher signal

B

Output no. 2 ( controlled device )

Type

0

Not installed

1

Relay, thermal relay, two position motor

Isolated Triac

2

Normally open thermal valve

Isolated Triac

3

Normally close thermal valve

Isolated Triac

4

"SSR" with 24 Vac input

Isolated Triac

5

"SSR" with 3-32 Vdc input

Pulsed 0/5 Vdc

C

Output no. 1 and 2 control mode

1

Heating, reverse acting, ( RA )

∗ Standard

2

Cooling, direct acting, ( DA )

3

Heating, RA ( no. 1 ) and cooling, DA ( no. 2 )

4

Cooling, DA ( no. 1 ) and heating, RA ( no. 2 )

D

Main control sensor location

1

Room, inside thermostat, or ( duct return air**)

∗ Standard

2

Duct supply air **

** Order with S60 or S70 sensor

E

Setpoint adjustment

1

User adjustable

∗ Standard

2

Blind cover

F

Scale

1

10

°C to 32 °C

∗ Standard

2

50

°F to 90 °F

3

-18

°C to 82 °C

4

0

°F to 180 °F

G

Output no. 3

1

Normally cooling, ( DA )

∗ Standard

2

Normally heating, ( RA )

H

Maximum running time of tri-state floating actuator

1

1 minute

2

2 minutes

...

etc.

9

9 minutes

Order Example: T560 - 75 - 41 - 12 - 12
One higher signal cooling output and one "SSR" 3-32 volts heating output.
Main sensor located inside the room. Setpoint adjustable by user.
Scale 50

°F to 90 °F. The output no. 3 is a damper with

a travel time of 2 minutes used in cooling mode.
∆ Note: These models have a vertical cover.
Note: remote sensor separately

WIRING

NOTE: TERMINALS 5, 6, 8, 9 AND 10 CAN BE WIRED TOGETHER

BETWEEN EACH THERMOSTAT IF POLARITY IS RESPECTED

Power supply 24 Vac -15% +10%

50/60 HZ 2 VA

COMMON

24 VAC

24VAC

5

6

POWER SUPPLY 24 Vac.

IMPORTANT: IF USING A COMMON TRANSFORMER
RESPECT POLARITY (COMMON AND 24 VAC)
BETWEEN EACH THERMOSTAT

Day night mode T560 only

CLOSE =

NIGHT

SET BACK

COMMON

INPUT

DAY / NIGHT 6

8

DAY NIGHT MODE

1 CONTACT USED FOR ALL

THERMOSTAT USING THE

SAME TRANSFORMER

Output #2 code A= 1, 2, 3 & 4 Triacs

RELAY OR THERMAL

VALVE 24 VAC

CONTACT

OUTPUT

3
4

OUTPUT #2 USING RELAY WITH ISOLATED TRANSFORMER

R

24VAC

Output #2 code A= 1, 2, 3 & 4 Triacs

RELAY OR

24 VAC

THERMAL VALVE

CONTACT

OUTPUT

COMMON

24 VAC

24VAC

5

6

OUTPUT #2 USING SAME TRANSFORMER TO OUTPUT

3

4

Output #1 code A= 5 Pulsed 0/5 Vdc

Output #2 code B= 5 Pulsed 0/5 Vdc

SOLID STATE

RELAY

3-32 VDC
TRIGGER

LOAD

COMMON

0/5 V

6

OUTPUT #1 AND/OR #2 USING PULSED 0/5 Vdc

AND / OR

4

10

USE TERMINALS 6 & 10 FOR OUTPUT #1
USE TERMINALS 4 & 6 FOR OUTPUT #2

Output #1 code A=6 & 7Analog 0 to 10 Vdc

0 TO 10 VDC

COMMON

0 TO 10 Vdc

6

10

OUTPUT #1 USING 0 TO 10 Vdc

ELECTRONIC ACTUATOR, SCR,
OR VOLTAGE RELAY

Output #3 Tri-State Floating

OPEN

CLOSE

24 Vac

DAMPER

ACTUATOR

OUTPUT #3

1
2

OUTPUT #3 TRI STATE FLOATING

COMMON

24 VAC 5

6

TRI STATE IF OPERATION OF THE ACTUATOR IS

REVERSED, FLIP REVERSING SWICH ON

ACTUATOR OR REVERSE WIRES #1 & #2

Remote main temperature control sensor

Room or return control code D= 1,

Supply control code D=2

EXTERNAL

SENSOR

NOTE: REMOVE

INTERNAL J4 JUMPER

7

REMOTE MAIN CONTROL SENSOR

COMMON

6

VICONICS

DUCT S60 OR S70

ROOM S80

IMMERSION S90

Power limit input

Analog 0 to 10 Vdc

LIMIT INPUT

0 TO 10 Vdc

COMMON

0 TO 10 Vdc

6

9

POWER LIMIT INPUT USING 0 TO 10 Vdc

ENERGY

SYSTEM

MANAGEMENT