Day night mode t266 only, Output #3 analog 0 to 10 vdc, Wiring – Viconics T266 User Manual

Page 2

background image

Page: 4

Page: 5

Page: 6

A

Output no. 1 ( controlled device )

Type

0

Not installed

1

Relay, thermal relay, two position motor

Isolated Triac

2

Normally open thermal valve

Isolated Triac

3

Normally close thermal valve

Isolated Triac

4

"SSR" with 24 Vac input

Isolated Triac

5

"SSR" with 3-32 Vdc input

Pulsed 0/5 Vdc

6

0 to 10 Vdc actuator, voltage relay or "SCR" *

0 to 10 Vdc

* If output #1 is ordered A=6, the change over input is not available

B

Output no. 2 ( controlled device )

Type

0

Not installed

1

Relay, thermal relay, two position motor

Isolated Triac

2

Normally open thermal valve

Isolated Triac

3

Normally close thermal valve

Isolated Triac

4

"SSR" with 24 Vac input

Isolated Triac

5

"SSR" with 3-32 Vdc input

Pulsed 0/5 Vdc

C

Output no. 1 and 2 control mode

1

Heating, reverse acting, ( RA )

∗ Standard

2

Cooling, direct acting, ( DA )

3

Heating, RA ( no. 1 ) and cooling, DA ( no. 2 )

4

Cooling, DA ( no. 1 ) and heating, RA ( no. 2 )

D

Main control sensor location

1

Room, inside thermostat, or ( duct return air**)

∗ Standard

2

Duct supply air **

** Order with S60 or S70 sensor

E

Setpoint adjustment

1

User adjustable

∗ Standard

2

Blind cover

F

Scale

1

10

°C to 32 °C

∗ Standard

2

50

°F to 90 °F

G

Output no. 3

Damper changeover input

1

Normally cooling, ( DA )

Common dry contact for all thermostats

2

Normally heating, ( RA )

Common dry contact for all thermostats

3

Automatic

Duct supply sensor **

4

Automatic
with recirculation

Duct supply sensor **

** Order with S60 or S70 sensor

H

Future option

0

Unused

∗ Standard

WIRING

NOTE: WITH THE PROPER CODES, TERMINALS 5, 6, 8 AND 9 CAN BE

WIRED TOGETHER BETWEEN EACH THERMOSTAT IF POLARITY IS RESPECTED

Power supply 24 Vac -15% +10%

50/60 HZ 2 VA

COMMON

24 VAC

24VAC

5
6

POWER SUPPLY 24 Vac.

IMPORTANT: IF USING A COMMON TRANSFORMER
RESPECT POLARITY (COMMON AND 24 VAC)
BETWEEN EACH THERMOSTAT

Day night mode T266 only

CLOSE =

NIGHT

SET BACK

COMMON

INPUT

DAY / NIGHT 6

8

DAY NIGHT MODE

1 CONTACT USED FOR ALL

THERMOSTAT USING THE

SAME TRANSFORMER

Output #1 code A= 1, 2, 3 & 4 Triacs

Output #2 code B= 1, 2, 3 & 4 Triacs

RELAY OR THERMAL

VALVE 24 VAC

CONTACT

OUTPUT

1
2

OUTPUT #1 AND/OR #2 USING RELAY WITH ISOLATED TRANSFORMER

R

24VAC

3
4

AND / OR

USE TERMINALS 3 & 4 FOR OUTPUT #1
USE TERMINALS 1 & 2 FOR OUTPUT #2

Output #1 code A= 1, 2, 3 & 4 Triacs

Output #2 code B= 1, 2, 3 & 4 Triacs

RELAY OR

24 VAC

THERMAL VALVE

CONTACT

OUTPUT

COMMON

24 VAC

24VAC

5

6

OUTPUT #1 AND/OR #2 USING SAME TRANSFORMER TO OUTPUT

3

4

AND / OR

1
2

USE TERMINALS 3 & 4 FOR OUTPUT #1
USE TERMINALS 1 & 2 FOR OUTPUT #2

Output #1 code A= 5 Pulsed 0/5 Vdc

Output #2 code B= 5 Pulsed 0/5 Vdc

SOLID STATE

RELAY

3-32 VDC
TRIGGER

LOAD

COMMON

0/5 V

6

OUTPUT #1 AND/OR #2 USING PULSED 0/5 Vdc

AND / OR

2

4

USE TERMINALS 4 & 6 FOR OUTPUT #1
USE TERMINALS 2 & 6 FOR OUTPUT #2

Output #1 code A=6 Analog 0 to 10 Vdc

0 TO 10 VDC

COMMON

0 TO 10 Vdc

6

4

OUTPUT #1 USING 0 TO 10 Vdc

ELECTRONIC ACTUATOR, SCR,
OR VOLTAGE RELAY

NOTE: IF OUTPUT #1 IS 0 TO 10 Vdc (CODE A=6)
CHANGE OVER IS NOT AVAILABLE

Output #3 Analog 0 to 10 Vdc

0 TO 10 VDC

COMMON

0 TO 10 Vdc

6

10

OUTPUT #3 USING 0 TO 10 Vdc

ELECTRONIC ACTUATOR, SCR,
OR VOLTAGE RELAY

Remote main temperature control sensor

Room or return control code D= 1,

Supply control code D=2

EXTERNAL

SENSOR

NOTE: REMOVE

INTERNAL J4 JUMPER

7

REMOTE MAIN CONTROL SENSOR

COMMON

6

VICONICS

DUCT S60 OR S70

ROOM S80

IMMERSION S90

Auto change over input.

1 supply sensor per thermostat

Automatic code G= 3

Automatic with recirculation code G= 4

AUTO CHANGE OVER INPUT WIRING: SUPPLY SENSOR

COMMON

INPUT

6

9

DUCT S60 OR S70

IMMERSION S90

NOTE: 1 SUPPLY SENSOR PER THERMOSTAT

Change over input. 1 dry contact for all

thermostat using the same transformer

Normally cooling code G= 1

Normally heating code G= 2

CLOSE = REVERSE
DAMPER OPERATION MODE

DIODE 1N4001

OR EQUIVALENT

COMMON

COMMON

INPUT

6

9

1 CONTACT FOR ALL THERMOSTAT

USING THE SAME TRANSFORMER

NOTE: IF 5 THERMOSTATS OR MORE ARE USED

ON THE SAME TRANSFOMER, INSTALL 1 DIODE
PER CHANGE OVER CONTACT

CHANGE OVER INPUT WIRING: CHANGE OVER THERMOSTAT