028-2005 M:\1_BINDER\01_MICROSTAT\01_English\07_Manual\T261ME03.DOC 3/21/03

THERMOSTAT WITH:

1 DAMPER MOTOR VOLTAGE OUTPUT 0 TO 10 Vdc

2 MORE OUTPUTS

POWER LIMIT INPUT

DAY-NIGHT MODE ( T261 ONLY )

TO OPEN THERMOSTAT COVER

Remove security screw on left side of thermostat cover.

Open up by pulling on the left side of thermostat.

THERMOSTAT INSTALLATION

A)

Location:
1- Shouldn’t be installed on outside wall.
2- Must be installed away from any heat source.
3- Shouldn’t be affected by direct sun radiation.
4- Nothing must restrain vertical air circulation to the thermostat.

B)

Installation:
1-

Pull out cables 6” out of the wall.

2-

Wall surface must be flat and clean.

3-

Separate the thermostat and the base by pulling cover on the left side (same
as the security screw.)

4-

Insert cable in the central hole of the base.

5-

Align the base and mark the location of the two mounting holes on the
wall.

6-

Install shields in the wall.

7-

Insert screws in mounting holes on each side of the base.
DO NOT OVERTIGHTEN!

8-

Open the cable protection 1 1/4 inch more or less.

9-

Strip each wire 1/4 inch.

10- Insert each wire according to wiring diagram.
11- Reinstall the cover ( right side first ).
12- Install security screw.

SETPOINT ADJUSTMENT KNOB LIMITATION

Note: To limit the rotation of setpoint knob, adjust setpoint to desired value, then
insert stoppers in appropriate holes.

Horizontal model:
S1,S10 = No limitation
S3 à S8 = Setpoint limitations

Vertical model:
S7,S10 = No limitation
S1 to S7, or S12: Setpoint limitations

REMOTE SENSOR

It is possible to use a remote sensor ( for duct or room application) by connecting it to
pins no. 6 and 7. Inside sensor must be disconnected by removing jumper J4 inside the
thermostat.

Characteristics of remote sensor 47 K

Ω.

180.0 °F

82.2 °C

5.494 Kohm

0.553 Volts

170.0 °F

76.7 °C

6.585 Kohm

0.648 Volts

160.0 °F

71.1 °C

7.933 Kohm

0.761 Volts

150.0 °F

65.6 °C

9.610 Kohm

0.893 Volts

140.0 °F

60.0 °C

11.700 Kohm

1.047 Volts

130.0 °F

54.4 °C

14.342 Kohm

1.225 Volts

120.0 °F

48.9 °C

17.682 Kohm

1.429 Volts

110.0 °F

43.3 °C

21.940 Kohm

1.659 Volts

100.0 °F

37.8 °C

27.412 Kohm

1.914 Volts

90.0 °F

32.2 °C

34.483 Kohm

2.191 Volts

80.0 °F

26.7 °C

43.704 Kohm

2.486 Volts

70.0 °F

21.1 °C

55.834 Kohm

2.791 Volts

60.0 °F

15.6 °C

71.866 Kohm

3.096 Volts

50.0 °F

10.0 °C

93.340 Kohm

3.393 Volts

40.0 °F

4.4 °C

122.298 Kohm

3.673 Volts

30.0 °F

-1.1 °C

161.670 Kohm

3.927 Volts

20.0 °F

-6.7 °C

215.805 Kohm

4.150 Volts

10.0 °F

-12.2 °C

291.100 Kohm

4.341 Volts

0.0 °F

-17.8 °C

396.830 Kohm

4.499 Volts

DAY-NIGHT MODE

An external contact closing between terminals 6 and 8 activates night mode. A LED
on the thermostat flashes continuously indicating night mode. By pressing the button
on the thermostat, day mode is reactivated. The thermostat returns to night mode when
pressing again the button, or automatically after a 4 hours delay.

Note: Terminals 6 and 8 can be connected together between thermostats.

POWER LIMIT INPUT

An external DC voltage applied between terminals no. 9 (+) et 6 (-), limits the

power permitted to outputs 1 and 2 only when these outputs are programmed as
heating. The following table gives the relationship between input voltage and the
allowed power for each output.

DC VOLTAGE

AT TERMINALS

NO 6 AND 9

MAXIMUM

POWER

OUTPUT 1

MAXIMUM

POWER

OUTPUT 2

MAXIMUM

POWER

TOTAL

0 volt

100 %

100 %

100 %

1 volt

100 %

100 %

100 %

2 volts

100 %

100 %

100 %

3 volts

100 %

80 %

90 %

4 volts

100 %

54 %

77 %

5 volts

100 %

28 %

64 %

6 volts

98 %

0 %

49 %

7 volts

68 %

0 %

34 %

8 volts

40 %

0 %

20 %

9 volts

18 %

0 %

9 %

10 volts

0 %

0 %

0 %

Note: Terminals 6 and 9 can be connected together between thermostats.

0 TO 10 VOLTS OUTPUT

Output no 3 (terminal no. 10) produces a DC voltage 0 to 10 volts generally used for
damper control. Minimum position of damper can be adjusted inside the thermostat
from 0 to 50 %, using a small screwdriver. Minimum and maximum positions can be
adjusted using the C263 programmer. Adjust LL parameter to desired minimum
position and HL to maximum desired position. LL and HL are preprogrammed at 0 (0
volt) and 100% (10 volts) at the factory. Adjusting LL and HL does not affect the
effective proportional band. Example: LL=20%, HL=80%, Pb=0.9

°C. damper will

modulate from 20 to 80 % on a 0.9

°C proportional band.

DIMENSIONS

0

180

135

90

45

F

VICONICS

5

4

3

2

1

10

9

8

7

6

114 mm

32 mm

( 71 mm )

( 71 mm )

2.8"

2.8"

( 114 mm )

( 83 mm )

4.5"

4.5"

1.275"

3.275"

COVER

SECURITY SCREW

OR FROM BACK

FROM TOP

WIRING

MODEL

VERTICAL

HORIZONTAL MODEL

BASE

T211
T261